Vs: Putkikoko/Modaus Lämpöpumpuissa /onko järkeä
DIY sanoi:
Tuo 2-3%:n öljymäärä itse lämpöpumpussa nestelinjan täytökseen nähden ei taida enää päteä näissä minispliteissä.Tuohan tarkoittaisi POE-öljynä vain <10g :aa per laite (tavoite >300g)!
Niin näyttäisi olevan oheisen perusteella:
http://www.mechanicalconceptsllc.com/downloads/Refrigerant%20Piping%20Manual.pdf
For HFC−410A recommended adding oil to system based on the amount of refrigerant charge in the
system. (
No need to add oil in systems with 20 lbs (<9kg) of refrigerant or less.
Samaisessa artikkelissa on valotettu tuota putkistovalintaa eri kanteilta.
Poimintaa:
A
major cause of compressor failure is liquid slugging.
Due to the additional refrigerant required to fill the lines, the likelihood
of slugging is greatly increased with lines over 50 feet (>15m) in length. It is
desirable to use the smallest liquid line that
will
not result in refrigerant flashing due to pressure drop.
Slugging<= "Humppaaminen" ?
slug = A column of liquid refrigerant returned to the compressor in the suction line. A slug which enters the compressor
can cause permanent compressor damage due to non−compressibility of liquids.
The liquid line must not directly contact the vapor line. If the refrigerant line plan results in a pressure drop of 20 psi (138kPa) or
more, the liquid line should be insulated in all places where it passes through an environment (such as an attic) which
experiences temperatures higher than the subcooled refrigerant (approximately 105F to 115F liquid at 95F ambient).
Refrigeration lines must not be buried in the ground unless they are insulated and waterproofed. Uninsulated copper
lines buried in wet soil or under concrete can cause serious capacity loss and erratic operation as well as early failure
due to corrosion.
Refrigerant velocity is not a consideration in the liquid line,
since the oil will mix completely with the liquid refrigerant.
Pressure loss is a consideration in the liquid line. If the pressure of the liquid refrigerant drops below its saturation temperature,some of the liquid will
flash into vapor to cool the remaining liquid refrigerant to the new saturation temperature. This can occur in a liquid line if the
pressure drops enough due to either
friction loss or
vertical lift.
Flash gas must be avoided in the liquid line. The only way to know for sure that a solid column of liquid is present at
the expansion device is to check subcooling.
A sight glass may be full of liquid, but bubbles can still form past the sight
glass. Flash gas at the expansion device can erode damage a TXV, can cause noise, and may cause starvation of the
evaporator coil.
Alternative Pipe Size
The risk of refrigerant slugging is increased and the smaller line will be
less costly.
The smaller line should be used.
(Vaihtoehdot tekstissä 5/8" ja 3/4" =>5/8" ok koska "pressure drop"vähäinen!
FIGURE flash gas in a liquid refrigerant line, liquid which has lost temperature and pressure to the point that gas bubbles begin
to form significantly reducing the efficiency of the system.
Flash gas can form as a result of friction losses or running the liquid line through areas
with extremely high ambients or both.
Hot gas bypass:
A form of capacity reduction. The system diverts hot discharge gas and liquid into the suction line bypassing
the evaporator coil. The most desirable form of hot gas bypass is the type which feeds hot gas into a side tap
on the distributor on the evaporator coil.
Slug:
A column of liquid refrigerant returned to the compressor in the suction line. A slug which enters the compressor
can cause permanent compressor damage due to non−compressibility of liquids.
Subcooling:
Cooling of refrigerant liquid below its saturated temperature while holding it at saturated pressure.
Superheat:
Heating of refrigerant gas above its saturated temperature while holding it at saturated pressure.
----------------------------------------------------------------
Ohessa kompressorivalmistaja BRISTOLIN:n antia aiheeseen:
http://www.bristolcompressors.com/Docs/Application%20Bulletin%20117.pdf
10.4
For cooling only systems,
oil return is critical only when the compressor is elevated above
the indoor coil.
For heat pump systems,
oil return is critical on the cooling cycle when the
compressor is located above the indoor coil and for heating, when the indoor coil is located above
the compressor.
It is desirable that short liquid traps be used at the bottom of any vertical upflow
field installed vapor lines (suction or discharge exceeding 10 feet (>3m) vertical) for both heating and
cooling cycles.
------------------------
Edelläesitettyyn perustuen ,en näe aihetta puuttua valmistajien putkistomitoituksiin ,jos niitä ei ole perstuntumalla kopioitu
esim. japsipumpuista.Kiinalaiset ovat oma lukunsa,joskus.
Aiheeseen nivoutuu kymmenien vuosien tutkimuspanos ainakin jäähdytysnäkökulmasta.Lämmityspuoli lienee vielä osittain hakusessa!