Chofulta 10 kW "mono-block" R410A invertteri VILP Ruotsin markkinoille AEYC-7134SVFU-CH2
Puhallinkin on invertteriohjattu. "Både fläkt och kompressor är inverterstyrda."
http://www.chofu.se/se/art/luftvatten.php
Esite (SE)
http://www.spotec.se/prodblad.aspx?fno=Produktblad_Chofu_Luft-Vatten.pdf
Käyttöohje (SE)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Instruction_Manual.pdf
Asennusohje (UK)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Installation_Manual.pdf
Service Manuaali (UK)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Service_Manual.pdf
Sulatusehtojen mukaan sulattelisi pakkasilla "kellon perässä" aina 35 min käynnin jälkeen. Ja pahimmillaan sulatus kestää 14 min. :-(
"Defrosting operation is controlled by the temperature of outdoor heat exchanger sensed by the thermistor and
the timer switch.
•• Defrosting operation starts when the both of the following conditions are met at the same time.
a)35 minutes’ of continuous run of the compressor after the start of heating operation or after the completion of
previous defrosting operation.
b)The temperature of the outdoor heat exchanger stays lower than -1.5°C continuously for two minutes.
•• Defrosting operating is called off if either of the following conditions is met.
a)The temperature of outdoor heat exchanger rises to 19°C while 4-way-valve is ON.
b)12 minutes has passed since compressor turned ON."
http://www.chofu.se/se/
Puhallinkin on invertteriohjattu. "Både fläkt och kompressor är inverterstyrda."

http://www.chofu.se/se/art/luftvatten.php
Esite (SE)
http://www.spotec.se/prodblad.aspx?fno=Produktblad_Chofu_Luft-Vatten.pdf
Käyttöohje (SE)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Instruction_Manual.pdf
Asennusohje (UK)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Installation_Manual.pdf
Service Manuaali (UK)
http://www.spotec.se/prodblad.aspx?fno=AEYC_Service_Manual.pdf
Sulatusehtojen mukaan sulattelisi pakkasilla "kellon perässä" aina 35 min käynnin jälkeen. Ja pahimmillaan sulatus kestää 14 min. :-(
"Defrosting operation is controlled by the temperature of outdoor heat exchanger sensed by the thermistor and
the timer switch.
•• Defrosting operation starts when the both of the following conditions are met at the same time.
a)35 minutes’ of continuous run of the compressor after the start of heating operation or after the completion of
previous defrosting operation.
b)The temperature of the outdoor heat exchanger stays lower than -1.5°C continuously for two minutes.
•• Defrosting operating is called off if either of the following conditions is met.
a)The temperature of outdoor heat exchanger rises to 19°C while 4-way-valve is ON.
b)12 minutes has passed since compressor turned ON."
http://www.chofu.se/se/