MSZ-LN sulatushuijaus

ThingWizard

Jäsen
Based on that 22:45 to 23 data I would suspect something strange is happening with the measurements.

I would suspect the shown temperature measurements to have a significant delta to what temperature the indoor unit itself perceives as the room temperature.

Perhaps the indoor unit isn't blowing air with the same speed or perhaps there is an air leak having an impact on the shown measurement.
Thank you, Interesting, however the temperature is taken from melcloud so that is the temperature the unit is seeing. I'm also logging fan speed and during that strange reading the fan speed was running constant at full speed. Well it's some kind of anomaly that's for sure.

I have been running with shorter runtimes now and more frequent defrosts and it seems like the unit is back in business again. I assume there was some severe icing it couldn't get rid of causing the power loss. It seems to have cleared that up now running shorter runs between defrosts. It's my guess.

Here are the curves for this afternoon. Red is garage temp, purple bars is power consumption, yellow is heat exhanger temperature. I don't see the same loss of heating power with defrosts running each hour. Additional power a while after defrost is reflected in garage temperature rise, (that was not the case last night)

Icing situation is when the heat exchanger temperature (yellow) falls below dewpoint temperature (blue). These periods are filled in with light blue. I'm logging dewpoint from weather.com to get an idea of the current icing conditions and when ice is being accumulated (theoretically) as that is affected by air pressure and humidity which the dewpoint data takes into consideration. So looking at the situation right now the icing periods are not that long, and I could probably relax the max runtime restrictions.

It's of course added complexity but it would be kinda cool i mitsurunner had a setting to download dewpoint data for the place where the pump is situated, and it could take this into consideration when calculating runtimes. However the current system normally works fine just as it is. I think we have had some extra humid air the last days causing extra bad icing conditions.

1771081374047.png
 

repomies

Hyperaktiivi
Mitsurunner doesn't have a lot of memory to play with at least when it runs in esp8266, so things like calculating dew point related matters would be better off done elsewhere, like perhaps Home Assistant. I suppose some sort of integral could be calculated in the microcontroller quite easily, if the current dew point could be fetched from somewhere. But there isn't much storage for history data, nor can it download big amounts of information without pushing it to the flash memory.
 

puu

Aktiivinen jäsen
Ja taas 10 puu-adapteria tehty viikonlopun aikana, ja yhä on viisi tilausjonossa. 30kpl olen tehnyt jo tänä vuonna. Menekkiä siis on ja hyvä niin!

Nyt olen mielestäni vastannut ainakin kaikille yhteyttä ottaneille. Mutta jos ei kuulu mitään, niin laita vaan uutta viestiä, saattaa joskus jäädä huomaamatta.

Nämä kun saan lähetettyä, niin siinä pitäisi olla kaikki 8.2. ja sitä ennen adapteria kyselleet katettu. Yritän muistaa laittaa aina viestiä kun olen laittanut postiin, mutta saattaa välillä unohtuakin. Eli tosiaan jos tuntuu että täältä päin ei kuulu mitään vaikka pitäisi, niin rohkeasti vaan viestiä.

1771166288524.png
 

haraldh

Vakionaama
Ei vaan mökin LN25 + LN35 jotka nyt CN105 ohjauksen saaneina ja sitä mukaa myös sulatuslaskurinkin myötä ilmenivät oireisiksi. Kun menee riittävän pakkaselle on sulatussykli 35 minuuttia.
 
Uusi MitsuRunnerin käytön aloittelija 👋 ilmoittautuu mukaan.

Wemos kortti saatu kasattua ja ohjelmisto / IoT Guru saatu myös toimimaan.
Vielä odotellaan Puun tekemää adapterijohtoa niin sitten pääsee asentamaan sitä mökillä olevaan LN25 pumppuun. Joka on nyt muutaman vuoden pyörinyt " hullun kierrolla " pitäen mökin juuri ja juuri + puolella.

Tällä hetkellä Mitsurunner loggailee ulkolämpöjä pihalla ja samalla näkee miten kortti käyttäytyy pakkasessa.
 
  • Tykkää
Reactions: iro

COLL

Tulokas
Hi all,

i've assembled the Wemos/Relay/Dallas sensor part of my Mitsurunner yesterday and today went on to flash the software.

My only problem right now:

If i run "esphome run hw_check.yaml" it only gets up to the part where it says "INFO Starting log output" and stays there indefinitely.

I even filled out all other yaml configs, which are working - the webinterface works, it is visible and connected to my local MQTT broker and even HomeAssistant autodetected the Mitsurunner Esphome device.

Just... i can't for the life of me get hw_check running so i can gather the DS18B20 sensor ids.

If i disconnect the board from USB, connect it again - it starts clicking on and off with the relay, so even that part is working properly.

If i "esphome run" or "esphome logs" again hw_check.yaml, it doesn't start clicking and never really starts the log output - i wonder what may be wrong?

I'd be grateful for any and all ideas...

OS is Linux Mint 22.3, Python 3.12.3

Config:

(venv) christian@christians:~/MitsuRunner$ cat hw_check.yaml
# Copyright (c) 2021 Veli Matti Lastumäki (Velsku at lampopumput.info),
# Joonas Ihonen (puu at lampopumput.info),
# Ilkka Roivainen (iro at lampopumput.info)
#
# Permission is hereby granted, free of charge, to any person obtaining
# a copy of this software and associated documentation files (the
# "Software"), to deal in the Software without restriction, including
# without limitation the rights to use, copy, modify, merge, publish,
# distribute, sublicense, and/or sell copies of the Software, and to
# permit persons to whom the Software is furnished to do so, subject to
# the following conditions:
#
# The above copyright notice and this permission notice shall be included
# in all copies or substantial portions of the Software.
#
# THE SOFTWARE IS PROVIDED "AS IS", WITHOUT WARRANTY OF ANY KIND,
# EXPRESS OR IMPLIED, INCLUDING BUT NOT LIMITED TO THE WARRANTIES OF
# MERCHANTABILITY, FITNESS FOR A PARTICULAR PURPOSE AND NONINFRINGEMENT.
# IN NO EVENT SHALL THE AUTHORS OR COPYRIGHT HOLDERS BE LIABLE FOR ANY
# CLAIM, DAMAGES OR OTHER LIABILITY, WHETHER IN AN ACTION OF CONTRACT,
# TORT OR OTHERWISE, ARISING FROM, OUT OF OR IN CONNECTION WITH THE
# SOFTWARE OR THE USE OR OTHER DEALINGS IN THE SOFTWARE.


# For Mitsurunnwer HW-verification, compatible with ESPHome version 2024.6.6 or newer
# Only for Wemos_HW (not for Sonoff Elite)
# Shows IDs of connected Dallas sensors
# Switches relay: 1sec on, 4sec off

esphome:
name: mitsurunner-hw-check
esp8266: # For Wemos
board: nodemcuv2 # For Wemos

substitutions:

# Set the GPIO-pins according to your HW-connections
dallas_pin: 'D2' # Pin for DS18B20 1-wire temperature sensors. Set to the pin number you are using.
relay_pin: 'D1' # Pin for controlling relay

# Dallas_IDs can be found in the logs, when the IDs are updated, the temperatures are shown in the logs
dallas_a: '0xaaaaaaaaaaaaaa28'
dallas_b: '0xbbbbbbbbbbbbbb28'

# Logs on
logger:
level: DEBUG
# Temperature sensor (Dallas DS18B20)
one_wire:
- platform: gpio
pin: $dallas_pin
# pin: D3 # dallas_pin


sensor:
- platform: dallas_temp
update_interval: 10s
name: "Dallas_1"
address: $dallas_a

- platform: dallas_temp
update_interval: 10s
name: "Dallas_2"
address: $dallas_b


# Relay PIN
switch:
- platform: gpio
pin: $relay_pin
name: "rele"
id: gpio_rele

status_led:
pin:
number: D4
inverted: True

# Turn relay ON/OFF
interval:
- interval: 5s

then:
- switch.turn_on: gpio_rele
- delay: 0.5s
- switch.turn_off: gpio_rele

Output:

(venv) christian@christians:~/MitsuRunner$ esphome run hw_check.yaml
INFO ESPHome 2026.1.5
INFO Reading configuration hw_check.yaml...
INFO Generating C++ source...
INFO Compiling app... Build path: /home/christian/MitsuRunner/.esphome/build/mitsurunner-hw-check
Processing mitsurunner-hw-check (board: nodemcuv2; framework: arduino; platform: platformio/espressif8266@4.2.1)
------------------------------------------------------------------------------------------------------------------------------------
HARDWARE: ESP8266 80MHz, 80KB RAM, 4MB Flash
ESPHome: Excluding Updater.cpp from build (using native OTA backend)
ESPHome: Excluding core_esp8266_waveform_phase.cpp from build (waveform not required)
ESPHome: Excluding core_esp8266_waveform_pwm.cpp from build (waveform not required)
No dependencies
Compiling .pioenvs/mitsurunner-hw-check/src/main.cpp.o
RAM: [=== ] 34.4% (used 28164 bytes from 81920 bytes)
Flash: [=== ] 26.9% (used 280891 bytes from 1044464 bytes)
=================================================== [SUCCESS] Took 2.57 seconds ===================================================
INFO Build Info: config_hash=0x44caf956 build_time_str=2026-02-16 17:18:59 +0100
INFO Successfully compiled program.
esptool v5.1.0
Connected to ESP8266 on /dev/ttyUSB0:
Chip type: ESP8266EX
Features: Wi-Fi, 160MHz
Crystal frequency: 26MHz
MAC: 58:bf:25:da:b0:53

Stub flasher running.
Changing baud rate to 460800...
Changed.

Configuring flash size...
Auto-detected flash size: 4MB
Flash will be erased from 0x00000000 to 0x00045fff...
Wrote 285040 bytes (208592 compressed) at 0x00000000 in 5.7 seconds (399.1 kbit/s).
Hash of data verified.

Hard resetting via RTS pin...
INFO Successfully uploaded program.
 
Viimeksi muokattu:

repomies

Hyperaktiivi
Sorry for not being able to help with the issue related to your linux setup. In windows the drivers had to be installed before the device was found, but after that it was ok. I suppose you must have the driver working fine in linux if you are able to flash the board. During flashing the board led blinks rapidly.

Here I have now witnessed my first wemos reset. 11066 minutes of uptime, and now I have a reset reason "Hardware watchdog" showing in my home assistant.
 

iro

Vakionaama
Hi all,

i've assembled the Wemos/Relay/Dallas sensor part of my Mitsurunner yesterday and today went on to flash the software.

My only problem right now:

If i run "esphome run hw_check.yaml" it only gets up to the part where it says "INFO Starting log output" and stays there indefinitely.

I even filled out all other yaml configs, which are working - the webinterface works, it is visible and connected to my local MQTT broker and even HomeAssistant autodetected the Mitsurunner Esphome device.

Just... i can't for the life of me get hw_check running so i can gather the DS18B20 sensor ids.

If i disconnect the board from USB, connect it again - it starts clicking on and off with the relay, so even that part is working properly.

If i "esphome run" or "esphome logs" again hw_check.yaml, it doesn't start clicking and never really starts the log output - i wonder what may be wrong?

I'd be grateful for any and all ideas...

OS is Linux Mint 22.3, Python 3.12.3

Config:



Output:

Using the code in the attachment, you can make DallasIDs appear in the WEB-server view. (At least I think so...)
 

Liitteet

  • DallasIDt.zip
    1,2 KB · Katsottu: 26

COLL

Tulokas
iro, thank you so much - this has worked.

And from what i can gather, i seem to have a "generic" problem with ESPHome, connected to my laptop - it never seems to complete the step after flashing and always seems to hang. If i unplug the ESP, plug it back in - only then it seems to execute whatever it was flashed.

To cut a long story short, i was able to extract the DS18B20 IDs thanks to your code!

Now, i successfully flashed it with MitsuRunner code and can see the heat readings, delta etc. - perfect :)

...on to the next challenge - installing it inside the heat pump!

Quick other question if i may: can anyone point me to a product to fix the heat sensors to the pipe in the "most neat way possible" - if possible without zipties :D

Or is it only possible to fix it with zipties due to the bend?
 

puu

Aktiivinen jäsen
Quick other question if i may: can anyone point me to a product to fix the heat sensors to the pipe in the "most neat way possible" - if possible without zipties :D

Or is it only possible to fix it with zipties due to the bend?
I don't know any better way to install than zip ties. Professionals have an old wisdom: "If zip ties aren't working, you're not using enough of them."

Here in the Finnish version of the wiki page are good pictures how to install the sensor and how not. Google translate seems to do good job here: https://mitsurunner.com/doku.php?id=fi:instructions_hw#anturien_asennus
 

iro

Vakionaama
Onko kokemusta miten Raspi/HA:n pärjäilee uusimman (tämän vuoden) ESPHome Buider-version kanssa ESP-imagen luomisessa ?
Minulla Windows läppärissä ESPHomen uusin versio veivaa Miturunnerin imagea kasaan 25 minuuttia ja generoi yli 600M:n työtiedoston.
 

HeTi

Aktiivinen jäsen
Onko kokemusta miten Raspi/HA:n pärjäilee uusimman (tämän vuoden) ESPHome Buider-version kanssa ESP-imagen luomisessa ?
Minulla Windows läppärissä ESPHomen uusin versio veivaa Miturunnerin imagea kasaan 25 minuuttia ja generoi yli 600M:n työtiedoston.
Home Assistantin lisäosana ESPHome 2026.2.0. toimii ihan ok. Muistia pitää olla 8G, joskus isoimmat esphomen käännökset ei enää onnistunut 4G-kortilla.
 
  • Tykkää
Reactions: iro

Osku1619

Tulokas
Tapahtuuko FT-35 huoneanturin siirto samalla tavalla kuin tässä ohjeessa? https://mitsurunner.com/doku.php?id=fi:indoor_thermistor

Minkälainen vastusarvotaulukko on tuolla huoneanturilla? Tuli pieniä haasteita autotallissa modbus-liitoksessa kun Procon a1m modbus-purkin alin lämpötila-asetus on 16c vaikka kaukosäätimestä voidaan asettaa tuo 8c joten funtsin teenkö anturin väliin vastushuijjauksen.

En tiiä pystyykö tuolla BMS Room Temperaturella tai BMS Virtual setpointilla sitten niin lahjakkaasti huijjaamaan laitetta että sen sais pitämään lämpötilaa sitten 10c. Nyt tein ohjelmallisen on/off ohjauksen 10c päälle ja 11c pois kun asetus on koko ajan se 16c. Eli käytännössä ainakun ovi aukaistaa niin lähtee päälle, muuten about pysyy lattialämmityksellä lämpimänä. Mutta olipahan ulkoyksikkö jäässä eli ei ainakaan tällä käytöllä oo tarvetta harventaa sulatuksia, päinvastoin...
 

Harrastelija

Vakionaama
MitsuRunnerista huolimatta Mitsu FT:n kanssa tulee tiheähköjä sulatuksia kun pakkasta on riittävästi.
Mitsun oma anturi ymmärtää pakkasta vain -15 asti?

Edit: HA ei ole saanut kerättyä mitsun oman anturin dataa moneen tuntiin. Siksi näyttää noin vaakasuoralta. Eikö mitsu tuota päivitä vai onkohan tiedonsiirrossa ollut ongelmia. Samaan aikaan sisälämpötilan mittaus on toiminut eli ei vaikuta tiedonsiirtovirheeltä. Anturi viallinen?

Edit2 Samoin käyttäytyy RW:n ulkoanturi. Pakkasella lukemat ei tule HA asti. Liekö melCloud filtteröi?

1771669612707.png

1771670167826.png
 
Viimeksi muokattu:

Harrastelija

Vakionaama
Onko kukaan kokeillut saako CN105 liitännän kautta järkeviä ulkolämpötiloja kovemmilla pakkasilla?
Vai lakkaako lukemat päivittymästä?
Jos pumppu itsekään ei saa lukemia niin mahdollisesti siirtyy johonkin climb modeen ja sulattelee varmuuden vuoksi?
 

haraldh

Vakionaama
Minulla on Wemos D1 mini levyn päällä relay hat. Se taitaa käyttää D1 pinniä, ja laitoin siis relay_pin: 5. Nyt kun homeassistantissa kokeilen niin en saa relettä naksumaan klikkaamalla rele-nappeja home assistantissa. Kai nämä releet nyt kuitenkin sormissa pitäisi tuntea?

dallaksen on D2 eli pin 4 ja ne toimivat joten uskon että sain nuo D-pinnit käännettyä oikein tuon avulla; https://forum.arduino.cc/t/esp8266-pins-mapping-d2-d3-d4-and-so-on/466758

Mutta miksi rele ei sano mitään?
 

wannabe

Aktiivinen jäsen
@Harrastelija Mulla Mitsurunnerilla turbotettu FT25 autotallissa pitää ylläpitolämpöä +13 ja näyttäs toimivan niin kuin pitääkin. Käy katkoa paljon, mutta löytyy myös pitkiä vetoja. Alla kuvat ottotehosta ja Mitsurunnerin mittaamista ukolämpötiloista tän kuun 12. päivältä. Säälisulatusväli 7h ja kovemmillakin pakkasilla vedellyt tuota 7h väliä. Pumpun oman ulkolämpötilananturin lukemista ei tietoa.

1771677995586.png


1771678060177.png
 

iro

Vakionaama
Minulla on Wemos D1 mini levyn päällä relay hat. Se taitaa käyttää D1 pinniä, ja laitoin siis relay_pin: 5. Nyt kun homeassistantissa kokeilen niin en saa relettä naksumaan klikkaamalla rele-nappeja home assistantissa. Kai nämä releet nyt kuitenkin sormissa pitäisi tuntea?

dallaksen on D2 eli pin 4 ja ne toimivat joten uskon että sain nuo D-pinnit käännettyä oikein tuon avulla; https://forum.arduino.cc/t/esp8266-pins-mapping-d2-d3-d4-and-so-on/466758

Mutta miksi rele ei sano mitään?
Jos käytät Wemos pinniä 1 niin muistaakseni tuo pitää määritellä näin (kaikki tavat käyvä)
relay_pin: D1
tai
relay_pin: 1
tai
relay_pin: GPIO5
 

Harrastelija

Vakionaama
Käy katkoa paljon, mutta löytyy myös pitkiä vetoja.
On kait tuossakin jotain outoa. Miksi kävisi katkoa 20 asteen pakkasella kun lauhemmalla käy tasaisesti useamman tunnin.
Nuo kyllä näyttää katkolta kun teho on nollassa pitkän aikaa (eikä vain piikkinä).
Onko tuolla muutakin lämmitystä jolloin pumppu menee katkolle?

Edit: Sulatuksessahan tulee kaksi piikkiä alaspäin tehon osalta. Ensin kun vaihdetaan venttiili jäähdytysasentoon (sulatus) ja toinen piikki kun käännetään takaisin lämmitykselle. Noiden alaspäin olevien piikkien välissä käydään korkeissa teholukemissa kun sulatetaan kompuralla.
Samoin lämmityksen alussa tulee kovat tehot kun kiritään lämpöjä takaisin asetuksen mukaisiin lukemiin.
 
Viimeksi muokattu:

wannabe

Aktiivinen jäsen
On kait tuossakin jotain outoa. Miksi kävisi katkoa 20 asteen pakkasella kun lauhemmalla käy tasaisesti useamman tunnin.
Nuo kyllä näyttää katkolta kun teho on nollassa pitkän aikaa (eikä vain piikkinä).
Onko tuolla muutakin lämmitystä jolloin pumppu menee katkolle?

En nää tuossa mitään outoa. Lähtee katkolaukalle noiden alkuryntäyksien ja sisäyksikön sijainnin vuoksi. Talli ei ole yksi avonainen tila. Pumppu 13 neliön työtilassa, josta puhaltaa varsinaisen tallin puolelle. Sisäyksikkö vastapäätä talliin johtavan oven kohdalla. Tallissa ei ole käytössä muuta lämmitystä.

Pistä pumppu ja runneri virrattomaksi vähäksi aikaa, jos vaikka se korjaisi tuon sun pumpun oudon yhteistyön runnerin kanssa.
 

Harrastelija

Vakionaama
Ei minullakaan enää ongelmia ole. Lauhtumisen myötä sulatukset venähti mitsurunnerin 3 tunnin säälisulatuksiin. Pari oikeaa mitsurunner sulatusta tarpeeseen tuolla näkyy. Ja pakkasta oli siis yli 20 astetta kun mitsurunner kävi -3 tilassa ja pumppu sulatteli omiaan.

Edit. Mutta pumpun oma ulkolämpötilamittaus näytti max 15 pakkasta ja tuon kovimman pakkasjakson aikana tuosta pumpun omasta anturista HA:han ei tullut mitään pakkaslukemia.
Samoin vastaavalle anturille näkyi käyneen RW:ssä (ei mitsurunneria kytkettynä). Ei lukemia moneen tuntiin. Tai lukema pysyi vakiona (-15) ja tietoa ei päivitetty.

1771682384327.png
 
Viimeksi muokattu:

iro

Vakionaama
Laitoin GPIO5 pinniksi, mutta kyllä tässä on jotain muuta. Jos relekortti on wemoksessa kiinni se ei lähde boottaamaan.
Asettako relekortti joitain Wemos-pinnejä ei-sallittuihin tiloihin jotka aiheuttavat ongelmia bootssa. Katso linkki
 

haraldh

Vakionaama
Onko kukaan kokeillut saako CN105 liitännän kautta järkeviä ulkolämpötiloja kovemmilla pakkasilla?
Vai lakkaako lukemat päivittymästä?
Jos pumppu itsekään ei saa lukemia niin mahdollisesti siirtyy johonkin climb modeen ja sulattelee varmuuden vuoksi?
Näyttää tosiaan siltä että CN105 liitännänä kautta saatava ulkolämpötla ei koskaan käy alle -15 °C. RW25. Huomaa miten sininen kuvaaja on aina tasainen -15 °C tasolla.

Screenshot at 2026-02-21 16-51-32.png
 

haraldh

Vakionaama
Asettako relekortti joitain Wemos-pinnejä ei-sallittuihin tiloihin jotka aiheuttavat ongelmia bootssa. Katso linkki
Pitää tutkia löydänkö jotan käyttöohjetta tjms tuolla Partcon myymälle relehatulle. Huomasin että Wemoksen omissa on nastoja joihin voi juottaa minkä pinnin haluaa ohjaavan, esimerkiksi jos haluaa käyttää kaksi korttia.

Miten selvitän jos tuo relekortti vetää esim D3 alas tai D4 ja/tai D8 ylös?

Muoks: Olisi ehkä kannattanut katsoa niitten pinnien labelit relekortista ja wemoksesta ennen juottamista. Tuon wikisivun mukaan jos tekee vain sokeasti niin että kääntää wemoksen samoin päin niin menee mun wemoksilla väärin. Mun wemos on peilikuva tuosta. Oppiihan tässä tosiaan.
 
Viimeksi muokattu:

iro

Vakionaama
Tapahtuuko FT-35 huoneanturin siirto samalla tavalla kuin tässä ohjeessa? https://mitsurunner.com/doku.php?id=fi:indoor_thermistor

Minkälainen vastusarvotaulukko on tuolla huoneanturilla? Tuli pieniä haasteita autotallissa modbus-liitoksessa kun Procon a1m modbus-purkin alin lämpötila-asetus on 16c vaikka kaukosäätimestä voidaan asettaa tuo 8c joten funtsin teenkö anturin väliin vastushuijjauksen.

En tiiä pystyykö tuolla BMS Room Temperaturella tai BMS Virtual setpointilla sitten niin lahjakkaasti huijjaamaan laitetta että sen sais pitämään lämpötilaa sitten 10c. Nyt tein ohjelmallisen on/off ohjauksen 10c päälle ja 11c pois kun asetus on koko ajan se 16c. Eli käytännössä ainakun ovi aukaistaa niin lähtee päälle, muuten about pysyy lattialämmityksellä lämpimänä. Mutta olipahan ulkoyksikkö jäässä eli ei ainakaan tällä käytöllä oo tarvetta harventaa sulatuksia, päinvastoin...
Yksi selitys käyttäytymiseen voisi olla että ulkolämpötilan ollessa alle -20C pumppu aloittaa kellosulatukset.
Ja "Japanin harmaapartaiset jotka ovat virittäneet sulatuslogiikkaa useiden vuosikymmenten ajan ja tietävät, mitä tekevät" ovat päättäneet toteuttaa sen sillä tavalla että suomalaiset Mitsu-hakkerit eivät pääse pilaamaan tätä pumpun toiminnan rampauttamista :)
 

iro

Vakionaama
Ei Mitsuissa ole ns. "kellosulatuksia" tietääkseni. :)
MItä nyt pidetään "kellosulatuksena". Jos jotakin sen tyypistä mekanismia ei ole niin kuivassa pakkasessa jolloin todellista sulatustarvetta ei juurikaan ole Mitsun pitäisi vetää kymmenien tuntien lämmitysjaksoja. Ja sitähän se ei tee.
 

janti

Moderaattori
Ylläpidon jäsen
MItä nyt pidetään "kellosulatuksena".
Sulatusohjelmassa on tietty aika jolloin sulatus laukeaa ajan mukaan, useasti tuo aikaraja on ulkolämpötilasta riippuva.
No onhan näissä se 2 h 30 min aikaraja siellä, uusimpien mallien sulatusohjelmista ei ole tietoa/kokemusta. :cool:
 
  • Tykkää
Reactions: iro

iro

Vakionaama
Tein Mitsurunneriin lisäosan joka mittaa lämmitysjakson pituutta (= kahden sulatuksen välistä aikaa). Tulokset talletetaan muistiin ja yhdeksän viimeisimmän lämmitysjakson pituus näytetään Mitsurunnerin WEB-näkymässä. Uusimman jakson indeksi on 1, vanhimman 9.

Saat tämä ominaisuuden käyttöön laittamalla oheinen tiedosto "heating_cycle" Mitsurunner-kääntäjän tiedostohakemistoon ja lisäämällä mitsu_conf.yaml tiedostoon rivi
...
heating_base: !include heating_cycle.yaml
...

EDIT: Liiteetiedostoa editoitu: "Heating periods" näytetään vain WEB-näkymässä , ei lähetetä Homeassiatntille.
 

Liitteet

  • WEB-näkymä.jpg
    WEB-näkymä.jpg
    111,5 KB · Katsottu: 22
  • heating_cycle.zip
    1,1 KB · Katsottu: 11
Viimeksi muokattu:

haraldh

Vakionaama
Sulatusohjelmassa on tietty aika jolloin sulatus laukeaa ajan mukaan, useasti tuo aikaraja on ulkolämpötilasta riippuva.
No onhan näissä se 2 h 30 min aikaraja siellä, uusimpien mallien sulatusohjelmista ei ole tietoa/kokemusta. :cool:
RW25 näyttää vetävän 2,5 h stinttejä.
 

Harrastelija

Vakionaama
Yksi selitys käyttäytymiseen voisi olla että ulkolämpötilan ollessa alle -20C pumppu aloittaa kellosulatukset.
Se on jännä että mistä pumppu tietää että on 20 pakkasta jos anturi näyttää max 15 pakkasta. Vai onko raja jo 15 kohdalla.
Nettiä yritin selata ja joku väite tuli vastaan että käyttävät anturia jonka luotettavuus loppuu -15 kohdalla ja sen vuoksi ei näy kylmempiä lukuja. En tiedä hylätäänkö kylmemmät lukemat vai näytetäänkö -15 anturilukemasta riippumatta.
 

janti

Moderaattori
Ylläpidon jäsen
Se on jännä että mistä pumppu tietää että on 20 pakkasta jos anturi näyttää max 15 pakkasta. Vai onko raja jo 15 kohdalla.
Nettiä yritin selata ja joku väite tuli vastaan että käyttävät anturia jonka luotettavuus loppuu -15 kohdalla ja sen vuoksi ei näy kylmempiä lukuja.

Tuossa anturikäyrää. Taitaa olla RT61, RT62 ja RT68 kaikki 15 kΩ @ 25 °C NTC antureita.
Tuota taidetaan suositella käytettäväksi -30C saakka.
1771764155400.png
 
Viimeksi muokattu:

wannabe

Aktiivinen jäsen
Kaivelin LN25 ja FT25 käppyröitä ja tän kuun 14. pv löyty pakkasta enemmän kuin -20 C ja molemmat pumput veti asetetut säälisulatusvälit. Eli ei taida ainakaan näissä olla sellasia kellosulatuksia, jotka ajaa Mitsurunnerin yli.

Ulkolämpötila Ruuvitag T

1771765219890.png


LN25 Power

1771765285144.png


LN25 Kennon T

1771765342950.png


FT25 Power

1771765386872.png


FT25 kennon T

1771765449669.png
 